BMC Operating Mode [Manual / Normal]
Ed Tanous
ed.tanous at intel.com
Wed Aug 14 07:03:16 AEST 2019
On 8/9/19 12:13 AM, vishwa wrote:
> Hi All,
>
> IBM systems have a need to run BMC either in Manual or Normal Mode. What
> it means is this:
>
> Manual: It's mostly a lab / debug mode, where in the system would be
> booted with recovery disabled.
> For example: If we enter Quiesce state as part of power-on, then BMC
> remains in Quiesce state and would *not* attempt to re power-on and
> reboot the system.
>
> Normal: This is the default customer mode with recovery enabled in BMC.
> For example: If we enter Quiesce state as part of power-on, then an
> attempt will automatically be done to re power-on and boot the system.
We have a very similar mechanism in our non-OpenBMC stack. We would
likely be interested in a generic interface for it, although the details
are different, as the BMC doesn't really monitor Quiesce, but the state
of the boot through ACPI and power rails.
>
> There are other use-cases, where BMC does a Automatic power-on after
> coming back from an AC loss. Manual / Normal would influence this.
This is classically a separate setting called "power restore policy". I
suspect you likely want to keep these separate as well, as the power
policy is something that a user is likely to set independent of
lab/debug/manual mode.
>
> My current thought is to make this a settings in phosphor-settings.
> Looking to see if others have any use-case like this.