Phosphor-fan-present only update fan Functional for xyz.openbmc_project.Inventory.Manager

Thu Nguyen thu at amperemail.onmicrosoft.com
Wed Dec 16 14:18:32 AEDT 2020


On 12/16/20 10:12, Matthew Barth wrote:
>
> On 12/15/20 9:01 PM, Thu Nguyen wrote:
>> Hi,
>>
>> I would like to ask about current behavior of phosphor-fan-present.
>>
>> When I unplug one fan, phosphor-fan-monitor will only update the 
>> Functional Dbus properties of 
>> /system/chassis/motherboard/FAN3_1/FAN3_1 and 
>> /system/chassis/motherboard/FAN3_1 of inventory interface to false.
>>
>> But not for "/xyz/openbmc_project/sensors/fan_tach/FAN3_1" of hwmon 
>> interface.
>>
>> Below is test log:
>>
>> ~# busctl get-property xyz.openbmc_project.Inventory.Manager 
>> /xyz/openbmc_project/inventory/system/chassis/motherboard/FAN4_2/FAN4_2 
>> xyz.openbmc_project.State.Decorator.OperationalStatus Functional
>> b false
>> ~# busctl get-property xyz.openbmc_project.Inventory.Manager 
>> /xyz/openbmc_project/inventory/system/chassis/motherboard/FAN4_2 
>> xyz.openbmc_project.State.Decorator.OperationalStatus Functional
>> b false
>> ~# busctl get-property xyz.openbmc_project.Hwmon-1644477290.Hwmon1 
>> /xyz/openbmc_project/sensors/fan_tach/FAN4_2 
>> xyz.openbmc_project.State.Decorator.OperationalStatus Functional
>> b true
>>
>> Is this the expected behavior?
>>
> Yes. The phosphor-fan-monitor application is configured to only update 
> the functional status of the fan (and/or individual fan rotors) within 
> inventory. This is separate than the functional state of the device 
> providing the tach sensors themselves since, for example, the sensor 
> can be correctly reporting 0 RPMs for a feedback speed, however that 
> should be shown as a nonfunctional fan needing to be replaced and not 
> the device providing the tach sensors of the fan.
>
>> Regards.
>>
>> Thu Nguyen.
>>
> Matt

It is clear.


Thank Matthew,

Thu Nguyen.