pid control configuration
Vijay Khemka
vijaykhemka at fb.com
Thu May 16 05:21:52 AEST 2019
On 5/13/19, 10:32 AM, "Ed Tanous" <ed.tanous at intel.com> wrote:
On 5/13/19 9:32 AM, Patrick Venture wrote:
> On Fri, May 10, 2019 at 2:21 PM Vijay Khemka <vijaykhemka at fb.com> wrote:
>>
>>
>>
>> On 5/6/19, 9:20 AM, "Ed Tanous" <ed.tanous at intel.com> wrote:
>>
>> On 5/2/19 4:24 PM, Vijay Khemka wrote:
>> > My understanding here is pid data are only defined for temp sensors which will generate pwm values for fan.
>> >
>>
>> The above is not how phosphor pid control operates. The temperature
>> controllers "request" a given fan RPM, then the fan PID controller
>> (which is scanned much more quickly than the temperature controllers)
>> attempts to drive the fan to that speed. This ends up being a two stage
>> feedback loop that can perform better than a single PID loop.
>>
>> Ed, we are not using cascade control here in facebook. We only use outer loop which gives data for fan to drive.
>> Is it possible to still run Phosphor pid controller with single loop?
>
> Your cascade PID could be a pass-through -- so that it receives the
> set-point from the sensor PID and then just sets it directly within
> that loop.. It may require a new PID controller that is just a
> pass-through to explicitly exist -- i haven't dove into
> phosphor-pid-control in a while, but you probably need to write a
> basically empty PID controller object type.
>
+1 That is an option for you.
Ed, please see if following declaration in entity manager would work as I am not defining any pid values here.
{
"Class": "fan",
"Inputs": [
"MB_FAN0_TACH"
],
"Name": "MB_FAN0_TACH",
"Outputs": [
"Pwm 1"
],
"Type": "Pid",
"Zones": [
"Pid 1"
]
},
>>
>> Regards
>> -Vijay
>>
More information about the openbmc