On Fri, May 10, 2019 at 2:21 PM Vijay Khemka <vijaykhemka at fb.com> wrote:
>
>
>
> On 5/6/19, 9:20 AM, "Ed Tanous" <ed.tanous at intel.com> wrote:
>
> On 5/2/19 4:24 PM, Vijay Khemka wrote:
> > My understanding here is pid data are only defined for temp sensors which will generate pwm values for fan.
> >
>
> The above is not how phosphor pid control operates. The temperature
> controllers "request" a given fan RPM, then the fan PID controller
> (which is scanned much more quickly than the temperature controllers)
> attempts to drive the fan to that speed. This ends up being a two stage
> feedback loop that can perform better than a single PID loop.
>
> Ed, we are not using cascade control here in facebook. We only use outer loop which gives data for fan to drive.
> Is it possible to still run Phosphor pid controller with single loop?
Your cascade PID could be a pass-through -- so that it receives the
set-point from the sensor PID and then just sets it directly within
that loop.. It may require a new PID controller that is just a
pass-through to explicitly exist -- i haven't dove into
phosphor-pid-control in a while, but you probably need to write a
basically empty PID controller object type.
>
> Regards
> -Vijay
>