Testing Phosphor-pid-control
Vijay Khemka
vijaykhemka at fb.com
Thu Jan 3 07:41:50 AEDT 2019
On 1/2/19, 11:05 AM, "Patrick Venture" <venture at google.com> wrote:
On Wed, Jan 2, 2019 at 11:00 AM Vijay Khemka <vijaykhemka at fb.com> wrote:
>
> Hi Patrick,
> I am not seeing any change in fan speed when I read hwmon values. Can you please give me any formula how it is using data to change speed. Because I tried faking several temperatures and finally could make this change when I bring temperature below 10 but it doesn't change when I take temperature to more than max value.
Which PID controller are you using? If you only have sensors
configured then there's nothing to push the changes, presumably you
have a PID added. Depending on which you chose, depends on what's
happening with it -- that's why I'm asking for more. The formula for
the "normal" pid controller is such that it tries to reduce the
"error" between the set-point and the real fan speeds.
I am using basic configuration for pid as below. I may have to revisit these data, please advise if I am missing anything here.
{
"Class": "fan",
"FFGainCoefficient": 0.01,
"FFOffCoefficient": 0.0,
"ICoefficient": 0.0,
"ILimitMax": 0.0,
"ILimitMin": 0.0,
"Inputs": [
"MB_FAN0_TACH"
],
"Name": "MB_FAN0_TACH",
"OutLimitMax": 100.0,
"OutLimitMin": 30.0,
"Outputs": [
"Pwm 1"
],
"PCoefficient": 0.0,
"SlewNeg": 0.0,
"SlewPos": 0.0,
"Type": "Pid",
"Zones": [
"Pid 1"
]
},
https://github.com/openbmc/phosphor-pid-control/blob/master/pid/ec/pid.cpp#L43
There's also a step-wise controller option, which is why I'm asking.
How to configure step-wise controller as we need for linear configuration as well.
>
> Regards
> -Vijay
>
> On 12/28/18, 1:50 AM, "Patrick Venture" <venture at google.com> wrote:
>
> On Thu, Dec 20, 2018 at 12:57 PM Vijay Khemka <vijaykhemka at fb.com> wrote:
> >
> > Hi Ed,
> > I am able to override and read it back but not seeing any change in pwm data as well as fan speed. I have swampd running.
>
> You mean the dbus reads of the values aren't changing? I'm not as
> familiar with the dbus-sensor integration beyond run-time
> configuration, versus run-time state. Swampd itself doesn't expose
> PID information or set-point information unless that's done in the
> step controller (and I didn't see that aspect in that object).
>
> Or are you saying that the fan speeds aren't changing when you read
> the hwmon values?
>
> >
> > Regards
> > -Vijay
> >
> > On 12/20/18, 10:14 AM, "Tanous, Ed" <ed.tanous at intel.com> wrote:
> >
> > Assuming you’re using dbus-sensors (which I’m pretty sure you are):
> >
> > Support for overriding sensor values was recently landed in this commit:
> > https://urldefense.proofpoint.com/v2/url?u=https-3A__gerrit.openbmc-2Dproject.xyz_-23_c_openbmc_dbus-2Dsensors_-2B_16177_&d=DwIGaQ&c=5VD0RTtNlTh3ycd41b3MUw&r=v9MU0Ki9pWnTXCWwjHPVgpnCR80vXkkcrIaqU7USl5g&m=1J-5eJl4Drc2LKcQ2SdONc02uR5cih3P68m66QcMYog&s=c9798qmI_pA3hnzB97oaYFK8yFTmwrxdpAeRrui4qkY&e=
> >
> > Overriding a sensor value with a "fake" sensor reading should be as easy as simply calling SetProperty on the dbus interface.
> >
> > Example as tested on my system (your path names may vary)
> > dbus-send --system --print-reply --dest=xyz.openbmc_project.CPUSensor /xyz/openbmc_project/sensors/temperature/Core_1_CPU0 org.freedesktop.DBus.Properties.Set string:xyz.openbmc_project.Sensor.Value string:Value variant:double:1.0
> >
> > and verify by reading it back out:
> >
> > dbus-send --system --print-reply --dest=xyz.openbmc_project.CPUSensor /xyz/openbmc_project/sensors/temperature/Core_1_CPU0 org.freedesktop.DBus.Properties.GetAll string:xyz.openbmc_project.Sensor.Value
> >
> >
>
>