[PATCH v2 1/4] dt-bindings: hwmon: pmbus: Add Maxim MAX31785 documentation
Rob Herring
robh at kernel.org
Fri Aug 11 02:13:31 AEST 2017
On Wed, Aug 02, 2017 at 04:45:38PM +0930, Andrew Jeffery wrote:
> Signed-off-by: Andrew Jeffery <andrew at aj.id.au>
> ---
> .../devicetree/bindings/hwmon/pmbus/max31785.txt | 126 +++++++++++++++++++++
> 1 file changed, 126 insertions(+)
> create mode 100644 Documentation/devicetree/bindings/hwmon/pmbus/max31785.txt
>
> diff --git a/Documentation/devicetree/bindings/hwmon/pmbus/max31785.txt b/Documentation/devicetree/bindings/hwmon/pmbus/max31785.txt
> new file mode 100644
> index 000000000000..8ddc4ea1958d
> --- /dev/null
> +++ b/Documentation/devicetree/bindings/hwmon/pmbus/max31785.txt
> @@ -0,0 +1,126 @@
> +Bindings for the Maxim MAX31785 Intelligent Fan Controller
> +==========================================================
This is the second fan controller binding I've seen recently. The other
being hwmon/aspeed-pwm-tacho.txt. I think some of this needs to be
common. There's only so many types of fans, right?
And we have the thermal binding which you don't appear to tie into.
> +
> +Reference:
> +[1] https://datasheets.maximintegrated.com/en/ds/MAX31785.pdf
> +
> +Required properties:
> +- compatible : One of "maxim,max31785" or "maxim,max31785a"
> +- reg : I2C address, one of 0x52, 0x53, 0x54, 0x55.
> +- #address-cells : Must be 1
> +- #size-cells : Must be 0
> +
> +Optional properties:
> +- use-stored-presence : Do not treat the devicetree description as canon for
Is this maxim specific? If so, needs a vendor prefix.
> + fan presence (the 'installed' bit of FAN_CONFIG_*).
> + Instead, rely on the on the default value store of
> + the device to populate it.
> +
> +Capabilities are configured through subnodes of the controller's node.
> +
> +Fans
> +----
> +
> +Only fans with subnodes present will be considered as installed. If
> +use-stored-presence is present in the parent node, then only fans that are both
> +defined in the devicetree and have their installed bit set are considered
> +installed.
> +
> +Required subnode properties:
> +- compatible : Must be "pmbus-fan"
What defines a pmbus-fan? Sounds generic, but then you have all these
maxim specific properties.
> +- reg : The PMBus page the properties apply to.
> +- maxim,fan-rotor-input : The type of rotor measurement provided to the
> + controller. Must be either "tach" for tachometer
> + pulses or "lock" for a locked-rotor signal.
> +- maxim,fan-lock-polarity: Required iff maxim,fan-rotor-input is "lock". Valid
> + values are "low" for active low, "high" for active
> + high.
> +
> +Optional subnode properties:
> +- fan-mode : "rpm" or "pwm". Default value is "pwm".
> +- tach-pulses : Tachometer pulses per revolution. Valid values are
> + 1, 2, 3 or 4. The default is 1.
> +- maxim,fan-no-fault-ramp: Do not ramp the fan to 100% PWM duty on detecting a
> + fan fault
> +- maxim,fan-startup : The number of rotations required before taking
> + emergency action for an unresponsive fan and driving
> + it with 100% or 0% PWM duty, depending on the state
> + of maxim,fan-no-fault-ramp. Valid values are 0
> + (automatic spin-up disabled), 2, 4, or 8. Default
> + value is 0.
> +- maxim,fan-health : Enable automated fan health check
> +- maxim,fan-ramp : Configures how fast the device ramps the PWM duty
> + cycle from one value to another. Valid values are 0
> + to 7 inclusive, with values 0 - 2 configuring a
> + 1000ms update rate and 1 - 3% duty respective duty
> + increase, and 3 - 7 a 200ms update rate with a 1 -
> + 5% respective duty increase. Default value is 0.
> +- maxim,fan-no-watchdog : Do not ramp fan to 100% PWM duty on failure to
> + update desired fan rate inside 10s. This implies
> + maxim,tmp-no-fault-ramp
> +- maxim,tmp-no-fault-ramp: Do not ramp fan to 100% PWM duty on temperature
> + sensor fault detection. This implies
> + maxim,fan-no-watchdog
> +- maxim,tmp-hysteresis : The temperature hysteresis used to determine
> + transitions to lower fan speed bands in the
> + temperature/fan rate lookup table. Valid values are
> + 2, 4, 6 or 8 (degrees celcius). Default value is 2.
> +- maxim,fan-dual-tach : Enable dual tachometer functionality
> +- maxim,fan-pwm-freq : The PWM frequency. Valid values are 30, 50, 100, 150
> + and 25000 (Hz). Default value is 30Hz.
> +- maxim,fan-lookup-table : A 16-element cell array of alternating temperature
> + and rate values representing the look up table. The
> + rate units are set through the fan-mode property.
> +- maxim,fan-fault-pin-mon: Ramp fans to 100% PWM duty when the FAULT pin is
> + asserted
> +
> +Temperature
> +-----------
> +
> +Required subnode properties:
> +- compatible : Must be "pmbus-temperature"
> +- reg : The PMBus page the properties apply to.
> +
> +Optional subnode properties:
> +- maxim,tmp-offset : Valid values are 0 - 30 (degrees celcius) inclusive.
> + Default value is 0.
> +- maxim,tmp-fans : An array of fan indexes whose fans are controlled by
> + the current temperature sensor. Fans are indexed from
> + zero. The valid values are 0 - 5 inclusive.
Why not use a phandle here.
> +
> +Example:
> + fan-max31785: max31785 at 52 {
> + reg = <0x52>;
> + compatible = "maxim,max31785";
> + #address-cells = <1>;
> + #size-cells = <0>;
> +
> + fan at 0 {
> + compatible = "pmbus-fan";
> + reg = <0>;
> + mode = "rpm";
> + tach-pulses = <1>;
> + maxim,fan-rotor-input = "tach";
> + maxim,fan-dual-tach;
> + };
> +
> + fan at 1 {
> + compatible = "pmbus-fan";
> + reg = <1>;
> + mode = "rpm";
> + tach-pulses = <1>;
> + maxim,fan-rotor-input = "tach";
> + maxim,tmp-hysteresis = <2>;
> + maxim,fan-lookup-table = <
> + /* Temperature RPM */
> + 0 1000
> + 10 2000
> + 20 3000
> + 30 4000
> + 40 5000
> + 50 6000
> + 60 7000
> + 70 8000
> + >;
> + };
> + };
> --
> 2.11.0
>